drathak

Posts: 5
Registered: 05/21/08
How to Model Complex Relays in Utility Industry?
Posted: Nov 3, 2009 6:43 PM
  Click to reply to this thread Reply
Hello All! I work for an electric distribution company and we are in the process of switching to ACAD Electrical.

I could use some guidance from you good folks about now. Something that I have been struggling with is how to model the IED relays we use. (Intelligent Electronic Device) From our perspective they are control relays, but rather than having one coil and so many NO and NC contacts, we have numerous current and potential sensing coils plus digital inputs and output contacts. Oh, and alarm contacts. All associated with one device.

How should something like that be handled? I’m leaning towards it being more like a PLC than a control relay. But we really glossed over the PLC stuff in our training since we didn’t think we’d need it. (Big mistake.)

What would be your suggested way of dealing with a complex device like that? I started off making the power supply the parent object (there is always just one) and created child symbols for the inputs and outputs, and have thoughts for doing the sensing coils, but all in all, I have a fear I’m heading down a bad path.

Does this seem reasonable or am I missing something? Would these be more like a PLC? They are programmable. My grasp of Electrical is just enough to be dangerous.

My fear is that there is something inherent in the program that I am going to break (or at least confuse) by not having NO & NC contacts for a "Control Relay". I mean, the output contacts can be operated remotely, so the parent "coil" doesn't really have any direct effect on that contact.

Can you good people point me to anyone that is doing this sort of thing and/or is using ACAD Electrical in the electric utility field?
Brad Coleman
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 3, 2009 11:11 PM   in response to: drathak in response to: drathak
  Click to reply to this thread Reply
I'm in a similar industry as we supply 11 & 33kV switchgear to some of the
government electrical agencies here in Australia.

What I do is similar. Create a parent block for the power supply inputs of
the relay. A large child block for the current/voltage inputs. I have used
two exploded terminals in another child block for discrete inputs after
suitable modifications and normal relay contacts for any switched contacts
in the IED.

All the blocks I have created are tied to a new table in the catalogue
database called PR (Protection Relays). As we use a relay, I add the
appropriate catalogue and pin list information to the appropriate databases.
When I tie the normal relay contacts to the parent device, ACADE asks if I
really want to move the contact from the relay family to the new PR family.
That is the only problem that will come up.
Electrical will not have any problems with contacts that are remotely
operated. All it really needs is the total number of contacts and what type
they are in the pin list database to check contact numbers and types are
exceeded or not. For more information on how to set the pin lists, lookup
Pin List in the electrical help and go to the advanced section.

You can modify the normal relay contacts and save the modified ones under a
new filename, but I find it easier just to use the normal relay contacts and
it won't break Electrical.

Regards Brad

wrote in message news:6282987@discussion.autodesk.com...
Hello All! I work for an electric distribution company and we are in the
process of switching to ACAD Electrical.

I could use some guidance from you good folks about now. Something that I
have been struggling with is how to model the IED relays we use.
(Intelligent Electronic Device) From our perspective they are control
relays, but rather than having one coil and so many NO and NC contacts, we
have numerous current and potential sensing coils plus digital inputs and
output contacts. Oh, and alarm contacts. All associated with one device.

How should something like that be handled? I'm leaning towards it being more
like a PLC than a control relay. But we really glossed over the PLC stuff
in our training since we didn't think we'd need it. (Big mistake.)

What would be your suggested way of dealing with a complex device like that?
I started off making the power supply the parent object (there is always
just one) and created child symbols for the inputs and outputs, and have
thoughts for doing the sensing coils, but all in all, I have a fear I'm
heading down a bad path.

Does this seem reasonable or am I missing something? Would these be more
like a PLC? They are programmable. My grasp of Electrical is just enough
to be dangerous.

My fear is that there is something inherent in the program that I am going
to break (or at least confuse) by not having NO & NC contacts for a "Control
Relay". I mean, the output contacts can be operated remotely, so the
parent "coil" doesn't really have any direct effect on that contact.

Can you good people point me to anyone that is doing this sort of thing
and/or is using ACAD Electrical in the electric utility field?
drathak

Posts: 5
Registered: 05/21/08
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 4, 2009 2:05 PM   in response to: Brad Coleman in response to: Brad Coleman
  Click to reply to this thread Reply
Guest wrote:
What I do is similar. Create a parent block for the power supply inputs of
the relay. A large child block for the current/voltage inputs.


Ah! Brilliant! Had not thought of that. Glad I asked first.

I have used
two exploded terminals in another child block for discrete inputs after
suitable modifications


Not sure I follow you here. What do you mean by "exploded terminals"? What I did was used the geometry we are used to and added all the necessary attributes in Symbol Builder. Seems to work so far.

All the blocks I have created are tied to a new table in the catalogue
database called PR (Protection Relays). As we use a relay, I add the
appropriate catalogue and pin list information to the appropriate databases.


Good info! But don't be surprised if I come back and ask for help doing that too. ;-)

When I tie the normal relay contacts to the parent device, ACADE asks if I
really want to move the contact from the relay family to the new PR family.
That is the only problem that will come up.


Do you think that would be the same if I'm creating them from scratch? Particularly if I'm creating them as a "PR" type instead of "CR"?

Electrical will not have any problems with contacts that are remotely
operated. All it really needs is the total number of contacts and what type
they are in the pin list database to check contact numbers and types are
exceeded or not. For more information on how to set the pin lists, lookup
Pin List in the electrical help and go to the advanced section.


I have looked at that some and think I understand. However, what contact type did you make the inputs in the pinlist? My best guess was 4 which means undefined. Then too, output contacts can be either NO or NC depending on their programming, so how did you set those?

Thanks again for all your input.
Brad Coleman
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 4, 2009 10:26 PM   in response to: drathak in response to: drathak
  Click to reply to this thread Reply
wrote in message news:6283439@discussion.autodesk.com...
Guest wrote:
What I do is similar. Create a parent block for the power supply inputs of
the relay. A large child block for the current/voltage inputs.


-Ah! Brilliant! Had not thought of that. Glad I asked first.

I have used
two exploded terminals in another child block for discrete inputs after
suitable modifications


-Not sure I follow you here. What do you mean by "exploded terminals"? What
I did was used the geometry we are used to and added all the necessary
attributes in Symbol Builder. Seems to work so far.

Basically, I inserted a terminal and exploded it. The copied the geometry
and needed wire connection points to give me 2 device terminals. Removed all
un-needed attributes and added the required attributes to make it a standard
child block. When I now insert the block, I now associate it to the parent
and have the XREF and such all show up as a proper child, but with no
contact symbol to confuse the issue, just what looks like two terminals to
represent the terminals on the device.

All the blocks I have created are tied to a new table in the catalogue
database called PR (Protection Relays). As we use a relay, I add the
appropriate catalogue and pin list information to the appropriate
databases.


-Good info! But don't be surprised if I come back and ask for help doing
that too. ;-)

When I tie the normal relay contacts to the parent device, ACADE asks if I
really want to move the contact from the relay family to the new PR
family.
That is the only problem that will come up.


-Do you think that would be the same if I'm creating them from scratch?
Particularly if I'm creating them as a "PR" type instead of "CR"?

If you create the blocks from scratch, you won't have a problem with ACADE
asking about the family. It would be easier to copy the existing relay
contact blocks, rename them and modify the family attribute default than to
redraw something that already exists. I thought why bother doing something
like that which is going to take up more room on the HDD when there are
blocks already done and which allow you to change the family with only a
question to answer when I do so.

Electrical will not have any problems with contacts that are remotely
operated. All it really needs is the total number of contacts and what
type
they are in the pin list database to check contact numbers and types are
exceeded or not. For more information on how to set the pin lists, lookup
Pin List in the electrical help and go to the advanced section.


-I have looked at that some and think I understand. However, what contact
type did you make the inputs in the pinlist? My best guess was 4 which
means undefined. Then too, output contacts can be either -NO or NC depending
on their programming, so how did you set those?

Yes, I did define the inputs using the 4 designation in the pinlist
database. Specifically 4I, 4V, 4T, 4M & 4C to differentiate the different
inputs. I & V for Current and Voltage. T, M & C for Trip, Monitoring &
Close. This allows the program to allocate the correct terminals to the
correct input as needed. The method is set out in the Electrical Help file
under Pin List -> Advanced

-Thanks again for all your input.

Not a problem.

Regards Brad
pjfontes

Posts: 70
Registered: 03/17/08
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 4, 2009 6:59 PM   in response to: drathak in response to: drathak
  Click to reply to this thread Reply
You are describing my biggest pet peeve with ACADE. Here's my solution:

For "multi-functional" relays (aka protection relays) we have a parent that shows all of the children graphpically.

I created a program to find the children and insert pointers on to the parent symbol - each function (including pwr) has it's own pointer. The child symbols (which are normal ACADE symbols) crossreference back to the parent via ACADE's XREF attribute.

see attached.
drathak

Posts: 5
Registered: 05/21/08
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 4, 2009 7:46 PM   in response to: pjfontes in response to: pjfontes
  Click to reply to this thread Reply
pjfontes wrote:
You are describing my biggest pet peeve with ACADE. Here's my solution:

For "multi-functional" relays (aka protection relays) we have a parent that shows all of the children graphpically.

I created a program to find the children and insert pointers on to the parent symbol - each function (including pwr) has it's own pointer. The child symbols (which are normal ACADE symbols) crossreference back to the parent via ACADE's XREF attribute.

see attached.


OK...I think I understand what you are doing here. Not clear on the why though. What advantage do you get by having the parent be a graphical representation of the overall device? I take it the parent isn't really used in your ladder, just nearby for reference? Not to mention the extra level of difficulty in having to have an additional program to locate the children and add pointers to them. Seems that defining a simple parent and children does away with that. In fact, I can't see why your large parent would need something outside the box to reference the children. (Ok. Maybe I do. If it's not on the ladder, there's no reference, right?)

Then too, I'm but a babe in these woods, so I'm certainly willing to see things your way if you can further explain it.

Edited by: drathak on Nov 4, 2009 1:48 PM
pjfontes

Posts: 70
Registered: 03/17/08
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 5, 2009 3:45 PM   in response to: drathak in response to: drathak
  Click to reply to this thread Reply
Why? Well, when you have a normal relay you always know where you parent AND your no/nc children are, the references locations of all of your children are right beside the parent symbol and the child symbols show you where their parents are. We try to follow this convention with multi-function relays. As an experiment, delete all of crossreferences on your 'normal' relay parents, submit a drawing, and then count the minutes before your phone rings. ;)

For multi-function relays you have to deal with more than just no/nc, there's no 'Home Base' (parent) to map out where all of your devices/functions are being used. I can look at my parent device and know exactly which functions are being used (no/nc/form-c contact, i.o etc) and where they are located in my 7-80+ page schematics. The parent device location is also a place where we put footnotes about settings and warnings related to the device.

We were using this method before we switched to ACADE, it was a huge improvement over the way we used to lay out protection relays. Since there's no equivalent functionality in out-of-box ACADE I modified the program to work with ACADE API and carried it over.

Believe it or not, the program is actually quite simple. We deal with a large volume of drawings so additional programs to get the job done are commonplace. You can contact me via p.a.u.l.f.o.n.t.e.s@yahoo.ca (no periods in name) if you want further explanation on the programming part.
Davidc1204

Posts: 25
Registered: 09/04/06
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 6, 2009 8:28 PM   in response to: pjfontes in response to: pjfontes
  Click to reply to this thread Reply
Hi Paul and all.

Like drthak I too have just started to look into using Protection Relays - so far GE models such as L90, C60 and F650 to name a few. Also like drthak I was looking at using the plc features to set up one of these - not at all straight forward! I'm pleased I checked the Forum and found this thread.

Paul, am understanding you correctly in that like Brad you create a Parent block and then child blocks for the associated I/O.

Do you work with fixed I/O Relays or modular like the GE relays if so how do you deal with the same base unit with different I/O modules.

My introduction to this area was a full substation control system comprising 10+ relay types with various I/O builds for each type, so currently I see more problems than solutions.

The drawing format you describe with the relays represented at the end at the drawing is how the drawings I have seen were done and I agree with you this is a good way to indicate the relay use throughout the drawing set. The drawings I saw were not produced by ACADE and were produced as two sets SCHEME and WIRING DIAGRAM. There were too many mistakes between the two sets for the wiring diagram to have been automated from the scheme.

This is where we need to improve things for our own work - getting a usable wiring schedule from the system.

Paul as you seem willing to receive emails re your program to pull child I/O references onto the parent block would you be willing to attach the code to a post on this forum then all people reading this can see your method without bothering you. If not is it OK for me to email you?
Like drthak I need to gather as much info as I can before I jump in with both feet (potentially both in one boot - and have to start all over again)
pjfontes

Posts: 70
Registered: 03/17/08
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 6, 2009 10:00 PM   in response to: Davidc1204 in response to: Davidc1204
  Click to reply to this thread Reply
David,

For GE relays (like the 369 for example) we offer 3 or 4 fixed configurations - we charge for custom configurations so rarely to customers request it. For us, having fixed configurations makes it easier for drawing automation, building circuits, and manufacturing of our products.

We are in the process up upgrading to ACADE so it's only a matter of time before we will need the ability to deal with modular protection relays. I'm not too worried about the day someone asks for this ability because the parent parts are a graphical representation... with some careful planning it shouldn't be too hard. (I wish I had time to whip up an example!)

I hesitate to post any of my code online because these are tools that I've made for my current employer.
Brad Coleman
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 9, 2009 12:23 AM   in response to: Davidc1204 in response to: Davidc1204
  Click to reply to this thread Reply
In electrical, you can set a Basic part in the catalogue and then add the
extra module's as additional components. This can be done at the catalogue
level or the component level. If the pin list database is setup, you can
have the proper pins used on the contacts and inputs for the various
modules.

That said, If the relay is modular, it sometimes has a different catalogue
number for the various versions (depending on the manufacturer). We don't
really use modular relays here all that much. When we do, I just type the
catalogue information in and bypass the Catalogue database and pin list
entirely. The majority of our customers supply their relays (getting their
government discount from the manufacturer) and all we get is the catalogue
number, contact/input information and manufacturer along with the relay. No
information on any optional cards that are added or not.

Regards Brad

wrote in message news:6285087@discussion.autodesk.com...
Hi Paul and all.

Like drthak I too have just started to look into using Protection Relays -
so far GE models such as L90, C60 and F650 to name a few. Also like drthak I
was looking at using the plc features to set up one of these - not at all
straight forward! I'm pleased I checked the Forum and found this thread.

Paul, am understanding you correctly in that like Brad you create a Parent
block and then child blocks for the associated I/O.

Do you work with fixed I/O Relays or modular like the GE relays if so how do
you deal with the same base unit with different I/O modules.

My introduction to this area was a full substation control system comprising
10+ relay types with various I/O builds for each type, so currently I see
more problems than solutions.

The drawing format you describe with the relays represented at the end at
the drawing is how the drawings I have seen were done and I agree with you
this is a good way to indicate the relay use throughout the drawing set. The
drawings I saw were not produced by ACADE and were produced as two sets
SCHEME and WIRING DIAGRAM. There were too many mistakes between the two sets
for the wiring diagram to have been automated from the scheme.

This is where we need to improve things for our own work - getting a usable
wiring schedule from the system.

Paul as you seem willing to receive emails re your program to pull child I/O
references onto the parent block would you be willing to attach the code to
a post on this forum then all people reading this can see your method
without bothering you. If not is it OK for me to email you?
Like drthak I need to gather as much info as I can before I jump in with
both feet (potentially both in one boot - and have to start all over again)
Davidc1204

Posts: 25
Registered: 09/04/06
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 9, 2009 8:05 PM   in response to: Brad Coleman in response to: Brad Coleman
  Click to reply to this thread Reply
Hi Brad,

Do you use relay layouts at the end of your drawing set like Paul does?
As a newbie to protection panels I have only seen one example of scheme drawings and they used this method it was hand updated and easily missed during drawing revisions.

Regards
David
Brad Coleman
Re: How to Model Complex Relays in Utility Industry?
Posted: Nov 10, 2009 12:35 AM   in response to: Davidc1204 in response to: Davidc1204
  Click to reply to this thread Reply
No, we don't have the relay layout on the dwgs. We utilize the XREF function
of electrical. That's were the co-ordinates of the contacts/inputs are
placed next to the parent block. At the child blocks there is a xref that
points back to the parent. Depending on the display choice, you can have a
graphical representation, table, and unused contacts can be displayed or
not.

As most of our relays are free issue by the client, they already have the
manuals in their hand. If we purchase and provide the relay, we insert
copies of the relay manuals into the manuals we provide.

We have only had to provide the relay layouts once to one customer, and they
used an extremely complicated system of drawings. They had 15 schematic
drawings for each panel, not including the relay layouts, labels, and tables
with all the fuses and terminals on them. I redrew their drawing and took it
all down to 2 schematics per panel (1 HV AC and DC control).

Regards Brad

wrote in message news:6285868@discussion.autodesk.com...
Hi Brad,

Do you use relay layouts at the end of your drawing set like Paul does?
As a newbie to protection panels I have only seen one example of scheme
drawings and they used this method it was hand updated and easily missed
during drawing revisions.

Regards
David